系统集成

P5 575机器一直报错,亮黄灯,请教原因和解决方法!

客户机房的9118-575之前9台都亮黄灯的,进HMC关了灯之后,现在有两台还是一直报错亮黄灯,报的错误是:BFE4C025,下面是报错内容和诊断信息:这是诊断信息:14002B81: Power/Cooling subsystem Unrecovered Error, bypassed with loss of          ...显示全部
客户机房的9118-575之前9台都亮黄灯的,进HMC关了灯之后,现在有两台还是一直报错亮黄灯,报的错误是:BFE4C025,下面是报错内容和诊断信息:

575报错.jpg




这是诊断信息:
14002B81: Power/Cooling subsystem Unrecovered Error, bypassed with loss of
            redundancy. Refer to the system service documentation for more  
            information.
           Additional Words: 2-91FF0002 3-01200000 4-00000000 5-00000000
                             6-00000000 7-00000000 8-00000000 9-00000000
           Error log information:
                 Date: Tue Nov 12 15:51:06 2013
                 Sequence number: 7384
                 Label: SCAN_ERROR_CHRP
    Priority: M  Maintainence Procedure: IQYRISM
    Priority: M  FRU: 41V0355 S/N: n/a CCIN: n/a Location:
    U9458.100.99204W8-P1-C4
    Priority: M  FRU: 12R7021 S/N: n/a CCIN: n/a Location:
    U9458.100.99204W8-P1-E1
    Priority: M  FRU: 41V0355 S/N: H10S7B55505 CCIN: 275D Location:
    U9458.100.99204W8-P2-C4
   Priority: A  FRU: 44P4083 Location:
    U9458.100.99204W8



看到里面指出了BPC和BPR,但是机柜上面的电源模块都是绿灯,看location也不知道是对应哪一个,求高手解救!!收起
参与33

查看其它 31 个回答haitian_160的回答

haitian_160haitian_160系统工程师dc
回复 20# haoxinfun

保存下profile,重置完以后每个分区重新指定下引导项!
危险这个很难说!
互联网服务 · 2013-12-02
浏览855

回答者

haitian_160
系统工程师dc
擅长领域: 服务器存储AIX

haitian_160 最近回答过的问题

回答状态

  • 发布时间:2013-12-02
  • 关注会员:1 人
  • 回答浏览:855
  • X社区推广