记录一次更换IBM P730电源模块的过程

在进行一天的机房日常巡检时,发现新上线不久的一台P730前面板有黄灯告警,由于没有HMC,所以登录系统进行如下操作:
1.errpt   发现有此报错
IDENTIFIER TIMESTAMP    T  C    RESOURCE_NAME    DESCRIPTION
51E537B5   0227091512  p  H       sysplanar0           platform_dump saved to file
291D64C3  0227091512   I   H      sysplanar0           platform_dump data
BFE4C025  0227091512   P  H      sysplanar0            UNDETERMINED ERROR
2.errpt -aj BFE4C025   看Description为电源或风扇失去冗余
3.再到机房打开机柜的后门观察小机,发现有一个电源的ac power LED 和dc power LED 一个灭了,一个是一闪一闪的,换一个电源线后问题依旧,所以上网找到如下信息,并确定是电源模块有问题。

Descriptions for the states of the power supply LEDs follow:

If both the ac power and dc power (green) LEDs are on solid (not flashing) and the error and identify function (amber) LED is off, the power supply is operating correctly. If the ac power LED is on, the dc power LED is flashing, and the error and identify function (amber) LED is off, then the system is turned off, but the power supply is still connected to the power source. If the error and identify function (amber) LED is flashing, the power supply is not operating correctly or the identify function has been selected.

4.查找机器的s/n号,打IBM 800报修

5.第二天配件到后,根据IBM硬件信息中的提示更换电源。为了保险起见,我先把主机上的应用切换到备机上--->shutdown主机-->下电-->换电源-->上电等待3分钟自检--->启操作系统--->起HA--->把应用切回主机---->测试应用正常---->换电源完毕


后记:因为是双电源,所以换电源本来是一个很简单的操作,即拔即插就行,完全可以下线操作。但是为了顺便测试一下HA,所以做以上操作。尽管整个过程耗时不多,但在切换过程中备机还是不能takeover RG,原因是Oracle的某些配置文件在主机上修改还没有在备机上同步修改,所以告戒所有系统管理员,HA是好,但是怎样让它好是你需要把握的。

参与12

11同行回答

youxiaoxu1020youxiaoxu1020软件开发工程师长益
楼主,您说的是具体哪些配置呢?我刚配了个HA下的oracle数据库,但是发现主机改动过的配置切换到备机上也都是改过的,你说的配置是主机和备机的系统参数的配置么显示全部
楼主,您说的是具体哪些配置呢?我刚配了个HA下的oracle数据库,但是发现主机改动过的配置切换到备机上也都是改过的,你说的配置是主机和备机的系统参数的配置么收起
互联网服务 · 2012-03-06
浏览2375

提问者

manganese_zh
系统工程师内蒙古包头
擅长领域: 服务器AIXUnix

相关问题

相关资料

问题状态

  • 发布时间:2012-03-06
  • 关注会员:1 人
  • 问题浏览:13348
  • 最近回答:2012-03-18
  • X社区推广