p595报错

P595报错
系统层面报错的详细信息
LABEL:          SCAN_ERROR_CHRP
IDENTIFIER:     BFE4C025

Date/Time:       Wed May 28 13:55:49 CST 2014
Sequence Number: 305
Machine Id:      00C37C554C00
Node Id:         p595a1
Class:           H
Type:            PERM
WPAR:            Global
Resource Name:   sysplanar0      
Resource Class:  planar
Resource Type:   sysplanar_rspc
Location:        

Description
UNDETERMINED ERROR

Failure Causes
UNDETERMINED

        Recommended Actions
        RUN SYSTEM DIAGNOSTICS.

HMC里面的报错信息
Platform Event Log - 51141F4D
Created at :        05/28/2014 05:54:08
Driver Name :        fips350/b1026a_1190.350
Subsystem :        Power/Cooling Subsystem
Event Severity :        Predictive Error
Action Flags :        Report to Operating System
        Service Action Required
        HMC Call Home
Action Status :        Reported to Opr Sys
        HMC-Acknowledged

       
Primary System Reference Code

       
Reference Code :        14010072
Hex Words 2 - 5 :        91FF0141 05230000 00000200 00000000
Hex Words 6 - 9 :        00000000 00000000 00000000 00000000

       

       
Normal Hardware FRU
Priority :        Mandatory, replace all with this type as a unit
Location Code :        U9A01.100.91801N0
Part Number :        ?FRU
CCIN :       
Serial Number :       
Machine Type Model :        9A01-100
Serial Number :        91801N0



51141F8F        2014-05-28 05:54:53        Power/Cooling Subsystem        Predictive Error        14010072
51141F4D        2014-05-28 05:54:08        Power/Cooling Subsystem        Predictive Error        14010072


Created at :        05/28/2014 05:54:53
Driver Name :        fips350/b1026a_1190.350
Subsystem :        Power/Cooling Subsystem
Event Severity :        Predictive Error
Action Flags :        Report to Operating System
        Service Action Required
        HMC Call Home
Action Status :        Reported to Opr Sys
        HMC-Acknowledged

       
Primary System Reference Code

       
Reference Code :        14010072
Hex Words 2 - 5 :        91FF0141 05230000 00000200 00000000
Hex Words 6 - 9 :        00000000 00000000 00000000 00000000

       

       
Normal Hardware FRU
Priority :        Mandatory, replace all with this type as a unit
Location Code :        U9A01.100.91801N0
Part Number :        ?FRU
CCIN :       
Serial Number :       
Machine Type Model :        9A01-100
Serial Number :        91801N0
参与12

11同行回答

aixmumu1260aixmumu1260系统工程师南瑞科技
14010072. 14010072. Explanation: The ambient room temperature is out of specification (to hot). The sensors are located in the. EPO panel and read/ converted ...显示全部
14010072. 14010072. Explanation: The ambient room temperature is out of specification (to hot). The sensors are located in the. EPO panel and read/ converted ...收起
互联网服务 · 2014-06-20
浏览2426
daigwdaigw系统工程师深圳融博
看看指示灯有没有电源风扇故障,可以升级一下微码再检查显示全部
看看指示灯有没有电源风扇故障,可以升级一下微码再检查收起
软件开发 · 2014-06-20
浏览2788
shenadamshenadam系统工程师sjo
Power/Cooling Subsystem显示全部
Power/Cooling Subsystem收起
互联网服务 · 2014-06-11
浏览2820
zhenzongjianzhenzongjian软件开发工程师na
晕死...以为啥东西坏了呢显示全部
晕死...

以为啥东西坏了呢收起
互联网服务 · 2014-06-10
浏览2823
VincentVincent存储工程师china
谢谢大家,是由于机房温度过高,导致的机器告警,现已正常,谢谢。显示全部
谢谢大家,是由于机房温度过高,导致的机器告警,现已正常,谢谢。收起
银行 · 2014-06-10
浏览2823
abit2007abit2007系统工程师代维
回复下,表示我关注过此帖,如果只是上面的信息,应该判断不了正确的部件。显示全部
回复下,表示我关注过此帖,

如果只是上面的信息,应该判断不了正确的部件。收起
互联网服务 · 2014-06-05
浏览2795
clvlbllclvlbll系统工程师IBM
ASMI里看看 看看DCA MDA什么的状态都正常嘛显示全部
ASMI里看看 看看DCA MDA什么的状态都正常嘛收起
互联网服务 · 2014-06-05
浏览2836
goodboy_wzlgoodboy_wzl系统运维工程师N/A
Un不好定位。其它硬件指示灯呢显示全部
Un不好定位。其它硬件指示灯呢收起
互联网服务 · 2014-06-02
浏览2788
VincentVincent存储工程师china
回复 3# whyexe     我感觉这个位置的标记有点不好找。显示全部
回复 3# whyexe


    我感觉这个位置的标记有点不好找。收起
银行 · 2014-05-30
浏览2794
whyexewhyexe存储架构师中国金融电子化公司
Bulk power controller (BPC)  看看U9A01.100.91801N0这个位置是什么再定位硬件显示全部
Bulk power controller (BPC)  看看U9A01.100.91801N0这个位置是什么再定位硬件收起
互联网服务 · 2014-05-30
浏览2788

提问者

Vincent
存储工程师china
擅长领域: 服务器存储灾备