今天有个p570电源模块发现后面的风扇声音很大,估计电源快挂了,打算提前给换了,之前更换都是电源失效后通过HMC管理和维护事件一步一步更换的,网上找到方法大家给点意见:
Model 9116-561 or 570 power supply

Learn how to remove and replace the power supply.

Attention: In order to use the power on procedure for this model you must check to see if you have one of the following adapters installed in slot P1-C6/C7. FC 1800 - HSL-2 Ports - 2 Copper FC 1801 - HSL-2 Ports - 2 Optical FC 1810 - GX Dual-port 4x HCAIs one of these adapters present in slot P1-C6/C7? Yes: Check for a label by the slot that indicates specifically that power supply concurrent maintenance is supported. If there is no label you must select the power off procedure to prevent system damage or data loss. If there is a label you can continue with the power on procedure.No: you can continue with the power on procedure.
Replace the model 9116-561 or 570 power supply with power on

Learn how to replace the power supply with the system power on.

The following procedure describes the replacement of the power supply while the system power is on. Attention: Two power supplies must be present in the system to power on the system unit. If one power supply fails, or you have a system failure that does not stop the fans, the system will continue to operate. You can remove and replace the power supply with the system power on if it is done in less than 5 minutes. After 5 minutes, the system will power off to prevent the system from overheating.


Exchange a part using the HMC Version 7 In the navigation area, expand Systems Management. Expand Servers. Select the managed system in which you are exchanging a part. In the Tasks area expand Serviceability. Expand Hardware. Select Exchange FRU. In the Replace Hardware - Replace FRU, Select FRU Type window select the system or enclosure in which you will exchange a part from the list. Select the type of part you will exchange from the menu and click Next. Select the location code of the part you will exchange from the menu and click Add.
http://publib.boulder.ibm.com/infocenter/powersys/v3r1m5/index.jsp?topic=/iphbd_p5/hmcreplace.htm

现在有个问题 我要更换的电源模块的FRU号我怎么能知道呢,电源模块的FRU号都是一样的

它的位置我是知道的,比如说Location: U7879.001.DQDGHYX-E2。

还有,上面的除外我还应该注意些什么

参与21

19同行回答

午夜幽魂午夜幽魂系统运维工程师计算机有限公司
过来学习一下,看人直接换过,没看到通过HMC是怎么换的,显示全部
过来学习一下,看人直接换过,没看到通过HMC是怎么换的,收起
系统集成 · 2011-10-08
浏览5247
becklynbecklyn系统工程师IBM
直接拔直接换显示全部
直接拔直接换收起
系统集成 · 2014-03-12
浏览4455
sleepsheep79sleepsheep79系统架构师HP
换p570 电源down机问题,我们已经碰到过两次了。以后还是关机换吧。显示全部
换p570 电源down机问题,我们已经碰到过两次了。以后还是关机换吧。收起
IT咨询服务 · 2012-12-13
浏览4490
gzhsjzgzhsjz系统工程师北京正群欣世信息技术有限公司
今天下午要去换570电源了。显示全部
今天下午要去换570电源了。收起
IT分销/经销 · 2012-03-28
浏览4579
cx9hcx9h工程师ibm
注意570 replace PS 中间时间间隔不能太长 90秒内最好显示全部
注意570 replace PS 中间时间间隔不能太长 90秒内最好收起
IT分销/经销 · 2012-03-19
浏览4623
max123567max123567软件开发工程师CSS
学习换电源显示全部
学习换电源收起
硬件生产 · 2012-03-18
浏览4552
uc804uc804数据库运维工程师企业
5分钟啊:L显示全部
5分钟啊:L收起
互联网服务 · 2012-03-17
浏览4538
nhuxynhuxy系统工程师浙江鸿程计算机系统有限公司
原来5minute内换是为了防止系统过热啊。显示全部
原来5minute内换是为了防止系统过热啊。收起
系统集成 · 2011-10-16
浏览4446
bbird006bbird006系统运维工程师OTA
换570电源还是谨慎点比较好显示全部
换570电源还是谨慎点比较好收起
互联网服务 · 2011-10-09
浏览4588
w_lei1983w_lei1983产品经理华为技术有限公司
对我就换570电源宕过一次机,而且宕机之后还起不来,我最后把FSP卡放电之后才能起来,多亏我那台570没有Lpar,之后我换都是关机换了显示全部
对我就换570电源宕过一次机,而且宕机之后还起不来,我最后把FSP卡放电之后才能起来,多亏我那台570没有Lpar,之后我换都是关机换了收起